Skip to main content
Cart

Supplementary reinforcement software issue

Posted by Davidalmost 4 years ago
Supplementary reinforcement software issue

Using the hilti software and having issues with a beam to concrete connection.

Getting the warning "Supplementary reinforcement is only allowed with static and seismic,anchor arrangements up to 9 anchors and with EN1992-4 and at least one finite edge",however I appear to be satisfying the requirements necessary.

1 Reply
Posted by Ask HILTI Teamalmost 4 years ago

Thanks for the question. Yes, that is correct the supplementary reinforcement will only work with the design concept of EC2 Part 4 therefore you connection will need to comply with the fixed anchor arrangements within the code and also the static and quasi static load conditions. We have a couple of webinars regarding this subject which covers designs in tension and shear which are free to watch and can be viewed in the 'Learn' section of this site. Should you then have any further questions then I'd suggest contacting your local HILTI technical department to discuss the connection.