Posted by Ilyaover 3 years ago
Supplementary rebar

I am struggling to make anchor fixing work ( failing on combination). Supplementary reinforcement is not helping a lot. Any ideas on how to improve it without changing the pad size? Thank you

supplementary reinforcement,anchor fixing

1 Reply
Posted by Ask HILTI Teamover 3 years ago

Thanks for the question and the PE file, assuming this hasn't been cast yet can you place some reinforcement to control cracking ? If you can select this option and your concrete now passes at less than 100% utilisation based upon a rigid baseplate option.


1 comment on this reply
Posted by Ilyaover 3 years ago
Thank you very much for your response.