Have found on US.hilti.com reference to title subject . values of shear/breakout & pull out seem to be for old hilti resins .
and don't reconcile with other comparative products. Can Hilti up-date their product information
Thank you for your enquiry. Assuming you are within Europe then the HY270 products European Technical Assessment lists the masonry units that have been tested . The published data may well be different to North America as there are different testing regimes and code criteria. I would suggest looking at the ETA below and if you can match your unit then you can use those values. If your unit is larger and of a higher compressive strength and you identify a unit close to it, then you would have a conservative value otherwise you would need to carry out testing to establish the allowable resistances in accordance with BS8539:2012.