Question about using Hilti filling set on the connection to the wall

Posted by Piotr Pienkowskialmost 2 years ago
Question about using Hilti filling set on the connection to the wall

Hello,
I need to design eccentric connection to the RC wall and hilti filling set needs to be used to make the connection to work. Is it possible to install the filling set on the connection to the vertical elements?

Anchor Installation,filling set

1 Reply
Posted by Ask HILTI Teamalmost 2 years ago

Thank you for your enquiry, yes it is possible to utilise the filling sets in vertical wall arrangement and overhead due to the viscosity of the HY200A V3 that is injected to fill the gap

filling set