Are anchor layouts editable in the masonry module of Hilti PROFIS?
Functionality appears to be limited; reviewing ETA-19-0160 (p23) there does not appear to be any reference to anchor layouts greater than 4No.
Are these limited due to testing procedures.
Attached is an example of proposed which requires verification; is this possible?
Appreciate any input; Thanks in advance.
Thank you for your question TCEng,
In the Masonry fixing part of PROFIS Engineering the anchors are editable according to what is defined by TR054. Single anchor, pair of anchors and group of four anchors in a rectangle. This is because a positive report from PROFIS Anchor always will have full support from relevant code. In “the real world” often we need a solution like the one you are suggesting using more than four Hilti HAS M12 HIT HY 270. Please contact my colleges at our local technical office in GB at gbtas@hiti.com.
