Posted by David Hodgsonabout 4 years ago
I only have 70 mm wall pank thickness
- I have a bracket to fix to a precast concrete wall plank. The plank has an insulated core and the outer concrete thickness is 70 mm. Loads are small. But i am unable to adopt the software as it calls for 100 mm minimum
1 Reply
Posted by Ask HILTI Teamabout 4 years ago
Thank you for your question. You are correct in that the minimum concrete thickness required in the Profis Engineering software is 80mm. I would suggest that as a way forward visiting your local HILTI website for the HUS3-6 range of concrete screw anchors and the technical data for redundant non-structural systems which contains design data for hollow core planks.