Skip to main content
Cart

How to fix error message below?

Posted by Robert Browneover 3 years ago
How to fix error message below?


The rebar is too close to the anchors (1). The minimum distance between the reinforcement rebar and the anchor is 20 mm and the minimum distance between the surface rebar and the anchor is 20 mm

supplementary,rebar anchors

1 Reply
Posted by Ask HILTI Teamover 3 years ago

Thanks for your question. I'm assuming you are using the supplementary reinforcement option in a concrete structure not yet cast. It is then just a case of moving the positioning of the proposed post installed anchor to meet the distance requirements . There is an option to apply a tolerance of reinforcement position in relation to the anchor in the software as well as amending the rebar spacing . Regarding the top cover this is taken as the minimum cover of 20mm for rebar.