Posted by Eleni Ntinopapaover 3 years ago
HAS-U anchors length
Hi,
Profis calculations have been made for HAS-U anchor rods embedment depth 600mm but I can see in the specification sheet these anchors go up to 510mm? Is this right?
thanks,
Eleni
1 Reply
Posted by Ask HILTI Teamover 3 years ago
Thank you for your question. You are correct, it is possible to produce calculations using Profis Engineering that are compliant with EC2 Part 4 . The code applies to fasteners that have a hef maximum of 20 x d i.e. M30 X 20 = 600mm hef is possible . The anchor rod elements that are found on the website are typically the most 'common' lengths 'off the shelf' though we can produce longer lengths if required.