Posted by Tom Green-Morganalmost 4 years ago
Brick Edge Failure - Hollow clay brick England Nostell Red Multi 102/65/215
I am designing some masonry fixings for a steel frame. When inputting in the shear force on the bolts, regardless of the value, i get a Brick Edge Failure of 250%.
I have tried changing the dimensions between the edge of the panel and the bolts, but the utilization does not change.
Loking at 'Shear load (ETAG 029 Annex C, Section C.5.2.2)', for hollow bricks, we should have a minimum of VRk,c,┴ = 1,25 kN shear resistance, but the hilti report specifies brick edge failure capacity of 0.2kN.
Could someone please shine some light on this please?
1 Reply
Posted by Ask HILTI Teamalmost 4 years ago
Thanks for the enquiry and the file. We will look into this and come back to you if that's ok?
2 comments on this reply
Posted by Ask HILTI Teamover 3 years ago
Thanks for your patience, I've looked into this matter for you and it is an error in the software. Thanks for bringing it to our attention and we will look to get it rectified for the next update. In the meantime, please feel free to use the online published data that we have attached.
Posted by Tom Green-Morganover 3 years ago
Yes, thank you! Much appreciate.