25mm standoff using shims instead of grout
Posted by Milo Gardnerabout 3 years ago
We are looking at a detail that was originally designed with no standoff. Now a 25mm standoff is required and the contractor is asking if they can build this out with steel shims. We have altered the Hilit Profis calc to include a 25mm standoff with grout (attached) and the bolts are still working fine, but there's no option to model shims instead. Would steel shims instead of grout alter the bolt calcs? Is there anything else to consider with shims as a replacement for a grouted solution?
Standoff,shim
Posted by Ask HILTI Teamabout 3 years ago
Thank you for your enquiry. Standoff with shims cannot be assumed as a grout, because with grout the assumption is that the concrete is taking up the compression loads. Our suggestion would be standoff without clamping.